[asterisk-biz] backup power requirements for emergency calling
Andrew Kohlsmith
akohlsmith-asterisk at benshaw.com
Fri Apr 14 14:51:35 MST 2006
On Friday 14 April 2006 14:18, calvis wrote:
> Takes 20 minutes for a generator to kick in? Sounds like you need an
> automatic transfer switch. My generator kicks in 20 seconds after a power
> outage with an automatic transfer switch.
Generally speaking you don't *want* your generator to kick in like that. You
want to ride out with UPS/battery until you've experienced a 20-30 minute
outage, at which point the outage is likely going to be a lengthy one and
THEN you want to start up the generator.
It's very common to do things this way, as generators aren't something that
really appreciate being cycled.
-A.